why is the lobby is not calculated in occupance load? the area is given 100 sf! @kiaragalicinao

question 6, real world practice PPD / calculating MEP systems, exercise A

---

<div class="post-metadata">

### Author: ![kiaragalicinao](https://yyz1.discourse-cdn.com/flex029/user_avatar/community.blackspectacles.com/kiaragalicinao/32/1607_2.png) [@kiaragalicinao](https://community.blackspectacles.com/u/kiaragalicinao)
#### Post date: [August 11, 2026, 8:21pm UTC](https://community.blackspectacles.com/t/occupant-load-question/7891/2 "2026-08-11T20:21:42Z")

</div>

Welcome to the Black Spectacles Community @mahsa_vanaki! Thanks for writing in.

The lobby is included in this occupant load calculation of 185 total occupants. It would be considered a business space, so you’d use a load factor of 150 sf/occupant, just like you would for the other spaces and their respective load factors.