Hi @wildlandguy - fire walls (table 706.4) are used to separate spaces into two separate buildings - they extend from foundation to parapet.
Table 508.4 is used when multiple occupancies are located in the same building, and provides the required separation between those occupancies.
Hope that was helpful and good luck on your next exam!
Thank you Chris. Yes that makes it crystal clear.